- Licensed Electrician
Single phase 200A service. Service disconnect is back to back to the panel inside with a short piece of EMT connecting them. Load side conductors and the GEC for the water pipe run through the EMT.
I am being told I need to add bond bushings. Is this true?
250.64(E) Enclosures for Grounding Electrode Conductors.
Ferrous metal enclosures for grounding electrode conduc-
tors shall be electrically continuous from the point of attach-
ment to cabinets or equipment to the grounding electrode
and shall be securely fastened to the ground clamp or fitting.