TRANSFORMER INSTALL 112.5 KVA 480 to 208Y/120

Status
Not open for further replies.

Part-Time

Member
Location
Houston, Texas
would this work for the installation from what i can tell some of the conduit is over sized but i think that was intentional
The supply wires will be about 400 feet long
480 TO 208Y 001.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Any of your conductors sized at 90? C are not code compliant since almost all terminations are only rated for 75? C.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Assuming the 480V supply is from a 200A OCPD, the feeder sizes appear compliant (assuming the tap lengths are OK.)

The transformer secondary conductors should be 4 conductors, not 3, and the #6 green should be #4 per 250.30(2) and 250.66.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Also the #6 EGC in the transformer primary feeder needs to be increased in size since the ungrounded conductors have been increased from a 150 amp-#1/0 to a 175 amp-#2/0.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Do the panels have mains ?
You might want to address the transformer GEC. (250.30)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
somewhat a mute point since the wire sizes are correct, but I would show the 75? rating rather than the 90? since that is what you are using and, yes, I would add the GEC to the electrode (and perhaps the bond jumper) rather than have one say "we wired it just like you showed"
 