Barrial depth..

Status
Not open for further replies.

Triton7

Member
Thank you sir, im running coax cable under ground into a house . table 830.47 , is the table i should be using with this application?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It is unlikely that Article 830 applies to this installation. What is the coax for? If for cable TV, then Article 820 applies, if for some thing else, then 800 or 725 would apply. There is no depth requirement in 725, 800 or 820.
 