T Triton7 Member Apr 5, 2012 #1 Coax cable installed outside underground has to be 24 inches In the depth according to 300.5. Correct?
Coax cable installed outside underground has to be 24 inches In the depth according to 300.5. Correct?
H Hv&Lv Senior Member Location - Occupation Engineer/Technician Apr 5, 2012 #2 Triton7 said: Coax cable installed outside underground has to be 24 inches In the depth according to 300.5. Correct? Click to expand... How about 830.47
Triton7 said: Coax cable installed outside underground has to be 24 inches In the depth according to 300.5. Correct? Click to expand... How about 830.47
T Triton7 Member Apr 5, 2012 #3 Thank you sir, im running coax cable under ground into a house . table 830.47 , is the table i should be using with this application?
Thank you sir, im running coax cable under ground into a house . table 830.47 , is the table i should be using with this application?
resistance Senior Member Location WA Apr 6, 2012 #4 Triton7 said: Thank you sir, im running coax cable under ground into a house . table 830.47 , is the table i should be using with this application? Click to expand... Yes!!!
Triton7 said: Thank you sir, im running coax cable under ground into a house . table 830.47 , is the table i should be using with this application? Click to expand... Yes!!!
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 6, 2012 #5 It is unlikely that Article 830 applies to this installation. What is the coax for? If for cable TV, then Article 820 applies, if for some thing else, then 800 or 725 would apply. There is no depth requirement in 725, 800 or 820.
It is unlikely that Article 830 applies to this installation. What is the coax for? If for cable TV, then Article 820 applies, if for some thing else, then 800 or 725 would apply. There is no depth requirement in 725, 800 or 820.