I am planning to consult an engineer before setting up an Primary 12KV switch to and set up a warehouse. How do engineers tend to go about pricing for their time...is there a variety of pricing available?
As others have said, it depends on the job.I am planning to consult an engineer before setting up an Primary 12KV switch to and set up a warehouse. How do engineers tend to go about pricing for their time...is there a variety of pricing available?
Our PE looks at the project, then quotes the cost
They need to be licensed in the state in which the job site is located. I have a friend who was at one time (may still be) licensed in all 50 states. So no, the engineer need not be local. As to whether I would want to visit a site before quoting a price, more often then not I would. But here again it depends on the scope of work. There may be complications that you are not considering. For example, when you say you will be setting a switch, that brings to mind such things as the concrete pad, a grounding system, underground ductbanks, the impact on the landscaping, the service entrance disconnect (if it is not the 12kV switch), fault current calculations, arc flash analyses, and a few other things. You need to decide how much of this stuff you want (or need) the engineer to deal with for you. That will often involve a preliminary conversation with the engineer, and that conversation is best held on site.Do engineers need to be local, or want to visit job sites before providing their quote.