Wall oven breaker size

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Okay I think I found the deal killer for a single oven.

T220.55 Note 4. Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance.

Had to cheat and read ALL the rules didn't you :D:D
(bet you even read instuction manuals )
 
Yes, I agree, knowing the code sections to look in to determine what rules are used to calculate what THE NEC requires is important, But I understand the manufacturer trumps the NEC. It can calculate out to 10 amps, if the manufacturer calls for 225 amp ocp that is what we need to provide. Right?

When I get a kitchen remodel call, I get the models of the ovens, ranges, and cooktops, etc. from the customer and find out from the manufacturer what they require. Fast, simple, (knock on wood) no errors.
 

tonype

Senior Member
Location
New Jersey
When I get a kitchen remodel call, I get the models of the ovens, ranges, and cooktops, etc. from the customer and find out from the manufacturer what they require. Fast, simple, (knock on wood) no errors.

I already wrote to the manufacturer
 