I've sent off the following to UL to see what they say.
2012 White Book index for "Hubs" refers to DWTT which in turn states "Fittings with internal female threads (e.g., hubs, conduit bodies, couplings) have only been investigated for use with threaded rigid conduit." and "All male threaded fittings and nipples have only been investigated for use with locknuts."
So does this mean I am violating the listing of the hub by threading a PVC TA into it and violating the listing of the PVC TA by threading it into the hub rather than holding it with a lock nut?
I have always been told mulitple times that a meyers hub is not UL listed and a sealing lock nut is not either so what is the correct way?
You would figure someone (manufacturer) would have picked up on this and would manufacture the proper fitting.
I mean, how often does one enter an enclosure with rmc or imc compared to entering it with "straight threads" from emt, pvc, seu/ser connectors.
Maybe I found my niche and will get into manufacturing this type of hub....................probably not.
Thanks for all the info.
Kind of like the raintight emt fittings that used to not really be raintight. Which BTW the new raintight ones are still a joke.
I've sent off the following to UL to see what they say.
2012 White Book index for "Hubs" refers to DWTT which in turn states "Fittings with internal female threads (e.g., hubs, conduit bodies, couplings) have only been investigated for use with threaded rigid conduit." and "All male threaded fittings and nipples have only been investigated for use with locknuts."
So does this mean I am violating the listing of the hub by threading a PVC TA into it and violating the listing of the PVC TA by threading it into the hub rather than holding it with a lock nut?
How about a female adapter on the PVC and a GRC nipple into a myers hub?
Sounds like a wasted effort but should be much closer to acceptable according to listings.
How about a female adapter on the PVC and a GRC nipple into a myers hub?
Sounds like a wasted effort but should be much closer to acceptable according to listings.
I'd go kicking and screaming before I did that.
If I couldn't do a myers hub, I'd use a sealing washer on an MA that had enough threads left to put a plastic bushing on.
I use them sometimes also - I save all the washers from liquidtight fittings or raintight EMT fittings or anything else that may have one yet it was installed in a location where it was not needed. Before anyone goes asking why I would take that washer away from its original fitting - what good does it do installed in the bottom of a 3R enclosure, or out of the lower side concentric / eccentric KO that is larger than the fitting? I have hundreds of these washers in 1/2 and 3/4 sizes.Sealing washer? I actually never used one before. Sealing locknuts yes but washers no. Do you have a link?