find transformer size when power factor is known

Status
Not open for further replies.

O'donisR

Member
Location
Miami
Hi everyone I'm new here, and I need help with the question below. I know the formula to get KVA for single phases transf KVA=(E x I / 1000) but i don't know what to do with the power factor data ? please help and thank you!!

:?

Question: What zise of transformer is requiered for a 100A, 240V, single phase noncontinuos load that has a power factor of 85%
  1. 15KVA
  2. 25KVA
  3. 37.50KVA
  4. 50KVA
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Your formula needs to include power factor, as follows: KVA=(E x I) / (pf x 1000)
In your example, KVA = (240 x 100) / (0.85 x 1000) = 28.2.
The next higher standard size (or so I believe) is 30 KVA. But the next higher choice in the list they gave you is 37.5 KVA. So I would select choice #3.

Welcome to the forum.
 

markstg

Senior Member
Location
Big Easy
Your formula needs to include power factor, as follows: KVA=(E x I) / (pf x 1000)
In your example, KVA = (240 x 100) / (0.85 x 1000) = 28.2.
The next higher standard size (or so I believe) is 30 KVA. But the next higher choice in the list they gave you is 37.5 KVA. So I would select choice #3.

Welcome to the forum.

Charlie,
KVA = V*I/1000
KW=V*I*PF/1000

pf is not needed to answer the question. 25KVA transformer....100A * 240V/1000 =24 KVA
 

Besoeker

Senior Member
Location
UK
pf is not needed to answer the question. 25KVA transformer....100A * 240V/1000 =24 KVA
A bit of a woopsie there from our PE...:)
Apologies, Mr Beck....

The basis of the 24kVA calculation is obvious. But does the "noncontinuos load" need to be considered?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
A bit of a woopsie there from our PE...:)
Apologies, Mr Beck....

The basis of the 24kVA calculation is obvious. But does the "noncontinuos load" need to be considered?
If it were an exam question as stated in the OP with respect to transformers, both power factor and "noncontinuous" loads are essentially red herrings.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
OK, memo to self: No posting on the forum allowed before the second cup of coffee.

Memo to O'donisR: Please ignore post #2, and pay attention instead to posts 4-6. Mea culpa.
 

Besoeker

Senior Member
Location
UK
OK, memo to self: No posting on the forum allowed before the second cup of coffee.

Memo to O'donisR: Please ignore post #2, and pay attention instead to posts 4-6. Mea culpa.
Beautifully and graciously put, that man!
:thumbsup:
 

Besoeker

Senior Member
Location
UK
If it were an exam question as stated in the OP with respect to transformers, both power factor and "noncontinuous" loads are essentially red herrings.
You're probably right. Certainly PF is irrelevant and thus a red herring.
And, if the question contained no information on duty cycle there would be no way to factor it in.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Well... The measurements are all fine and dandy of course, but every one of you know when I drive up I am going to hang a 15, but only because we don't hang 10's anymore...:lol:
 