Roger and Jumper,
Thanks for your prompt response.
 I have spent more than a little time reviewing Table 210.21(B)(3) and think I understand it. I know that a 50A receptacle is required on a 50A circuit. The question is "Can I put a 50A plug on any device that I want to (assuming that it requires less than 50A), and use it on a 50A circuit?"
Of course you can. There may or may not be some safety issues involved, but you can do it and it would work.
			A 30A device with UL listing may come with a 30A plug. Am I violating anything if I remove that plug and replace it with a 50A plug and use it on a 50A circuit? Does the fact that it is UL listed change anything?
Whether or not it is UL listed does not seem to me to figure into the equation at all. I am not sure just what you would be violating. It certainly would not be in accordance with the manufacturer's instructions but a device that is plug and cord connected like this is not a device directly subject to the NEC, any more than a toaster is. The outlet the toaster plugs into is subject to NEC whims, but not the toaster itself.
There may or may not be safety issues associated with doing something like this. Realistically, the chance of this going bad on you is very low.
If your situation involves OSHA, you may have some issues with them. In a very legalistic sense what you are doing probably is a violation of something. It is probably not in and of itself "unsafe". The worst argument I can come up with is that it is slightly possible that the cord set that came with the clock is lightweight enough that it might not trip the 50A CB protecting this branch circuit if the cord or the clock were to short circuit and that might eventually lead to a fire due to overheating of the cord. How likely such a thing is, I don't know. Seems pretty low on the totem pole of things to worry about.
There might also potentially be an issue with the cord conductor size not mating up well with the new 50A plug that might cause some kind of problem.
There are probably ways that this can be accomplished that would not involve doing so in a suspect way, and in an environment subject to potential OSHA inspections, I would be looking to do so.
Incidentally, the circuit breakers are there to protect the premises wiring, not whatever is plugged into an outlet.
One thing I would suggest is that you are being very vague about what it is you actually want to do and that makes all of us a little nervous in the first place.