I should add there are three basic means of protecting conductors in a circuit (including after the receptacle)
Limiting of the load that can be connected by user.
Providing over current protection ahead or down stream of a conductor
and fault current protection that always has to be ahead of the conductor it is protecting.
The last one is where there is a problem in protecting appliances that was design for lower current sized circuits but used on larger size circuits.
Limiting of the load that can be connected by user.
Providing over current protection ahead or down stream of a conductor
and fault current protection that always has to be ahead of the conductor it is protecting.
The last one is where there is a problem in protecting appliances that was design for lower current sized circuits but used on larger size circuits.