jumper
- 3 Hr 2 Min from Winged Horses
Let's not do that and continue the fun![]()
So, what did the inspector say? Inquiring minds wanna know.
:? I thought we were talking about connecting the inter-system bonding grid to a piece of #6 going to a ground rod instead of directly to the service enclosure.
Is the question under discussion about hooking the inter-system bonding device right, smack on the ground rod?
Ok, went back and read over the posts.
So we have a #6 GEC from the main down to a ground rod, then we have a second #6 coming back up from the ground rod and the inter-system terminal is attached. Am I right?
maybe if the connection to the rod is irreversible
The GEC is continuous... just passes through the acorn clamp. What did I miss?
Pete
Pete
I think your way definitely meets 250.94(4). I think iwire was saying if it is a seperate clamp then maybe irreversible connection to the rod would be OK.
This is correct, the problem is that the #6 is not the GEC. The rod in question does have the GEC attached though.
So... how about the GEC is continuous from the service equipment through the acorn clamp on the rod and a tail long enough to reach the IBJ is utilized... we are still technically making the attachment to the actual GEC.
Pete
I just misunderstood what he was describing.
I thought he was being cute and trying to call the rod itself a 'GEC'.![]()
Glad it passed. While I misread your OP, I still agree that the install is ok. Is a acorn clamp inferior to a split bolt seems to be the only issue left to debate.
The install as it was done is a code violation regardless of it passing or working fine.
Thanks for the input, next time I'll make sure I connect the IBT correctly :happyyes:
The device I used was like the one pictured. The problem, the GEC is too low and there was not enough room to connect the IBT and attach it to the House.