Benton Senior Member Location Louisiana May 24, 2012 #1 I have a 20 amp circuit can I splice number 14 off of it to feed lights. What I'm asking is can I come off of a receptacle that's being fed by 20 amp circuit with number 14 wire to be a light switch and lights?
I have a 20 amp circuit can I splice number 14 off of it to feed lights. What I'm asking is can I come off of a receptacle that's being fed by 20 amp circuit with number 14 wire to be a light switch and lights?
Benton Senior Member Location Louisiana May 24, 2012 #2 I only ask this question because I'm trying to prove a point to my customer who wanted to buy all the material and dictate everything.
I only ask this question because I'm trying to prove a point to my customer who wanted to buy all the material and dictate everything.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) May 24, 2012 #3 No. Not unless you can change the overcurrent device on the entire circuit to 15 amps. You must protect the conductors in accordance with 240.4
No. Not unless you can change the overcurrent device on the entire circuit to 15 amps. You must protect the conductors in accordance with 240.4
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 24, 2012 #4 Benton said: I only ask this question because I'm trying to prove a point to my customer who wanted to buy all the material and dictate everything. Click to expand... Never let the customer dictate the wiring. This is cover in our FAQ's http://forums.mikeholt.com/showthread.php?t=83435&p=649529#post649529
Benton said: I only ask this question because I'm trying to prove a point to my customer who wanted to buy all the material and dictate everything. Click to expand... Never let the customer dictate the wiring. This is cover in our FAQ's http://forums.mikeholt.com/showthread.php?t=83435&p=649529#post649529