- Licensed Electrician
FPN are not enforcible.
210.19 Conductors ? Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
FPN No. 4: Conductors for branch circuits as defined inArticle 100, sized to prevent a voltage drop exceeding3 percent at the farthest outlet of power, heating, and lightingloads, or combinations of such loads, and where themaximum total voltage drop on both feeders and branchcircuits to the farthest outlet does not exceed 5 percent,provide reasonable efficiency of operation. See FPN No. 2of 215.2(A)(3) for voltage drop on feeder conductors.
NEC has specified percentages of voltage drop!
Transforming it should be cheaper.
no, there are actually 3 wires. two hots and a neutral, and a #12 ground.
I'd verify that 7 amps figure... I can't imagine any wireless equipment drawing over 800 watts. The transmitter itself should be a couple watts at the most, and the smarts should only draw around 100W.
We did a wireless mesh network on the golf course. 400+ acres served by 11 towers, which were powered from the irrigation control system. Each tower consists of two Colubris access points (1 dual channel; 3 radios total) and a 1000 mW amplifier mounted on a fiberglass pole in a weatherproof enclosure.
One of the irrigation power circuits feeds 6 towers, plus a dozen Toro irrigation satellites. The circuit capacity is only 20A 120V and I'd estimate the load is 15A. There are also a couple 15A circuits that feed 1-2 towers and 4-5 satellites.
building is 770' x 1600'.
there are three repeaters, 7 amps. i checked.
i'm setting a subpanel 600' from the main switchgear,
and the plug is 500' from THAT. subpanel is fed by a
15kva xfmr on wall above panel. 480 volt 3 ph feed to
xfmr. 1/0 compact aluminum feeding the xfmr.
it's a wireless pick system with screens on the forklifts.
#6 it is for the branch circuit... it'll all work out. i originally
swagged it as a #10 without bothering to measure.
you have a dumb head, the wallet suffers.
on a positive note, i got 750' of 1 1/2" emt installed 30'
up in the air between 8 am and 12:30. called it a day.
mostly straight, some 4 point saddles, and whatnot, but
it went quick.
Fast- you must of been going full throttle.on a positive note, i got 750' of 1 1/2" emt installed 30'
it went quick.
missed a 120 volt receptacle on a bid.
30' up in the air, feeding a wifi repeater.
7 amp load.
Other than for fire pumps and maybe a couple of other things the NEC does not have voltage drop limitations.
But local code may. The Florida building code limits voltage drop throughout the state for example.
What is their limit?
Did we ever hear what size wire the plans call for?
Most jobs I've bid tell you the wire size somewhere.
the prints will call for two #6 and #8 ground.
If this is a 20 amp circuit and conductor size is increased to #6 for voltage drop purposes then the equipment grounding conductor also needs to be increased to #6.
If this is a 60 amp circuit using 6 AWG conductors - the equipment grounding conductor can be 10 AWG.
Just doesn't quite sound right does it? But that is what code says.
A code compliant way to use the 10 AWG EGC is to run a feeder to near the outlet with 10AWG EGC. Then run shorter 20 amp branch circuit to the outlet with smaller conductors.
I disagree. The EGC only has to be increased in size proportionately when the ungrounded conductors are upsized, not to the same size as the ungrounded conductors. See 250.122(B)