what year: grounds and neutrals on seperate bars in sub panels?

Status
Not open for further replies.

68Malibu383

Member
Location
Raleigh, NC
Odd. Most houses (I'd guess 90%) I inspect in NC built in the 60's and prior have a three wire (or two, if you'd like) feed (two hots and a neutral) from the main panel to the sub panel. No ground wire and only one buss bar for both neutrals and grounds.
 

480sparky

Senior Member
Location
Iowegia
1968 contained a new article, 384-27. It is now 408.20.

I have compiled a database of certain Code references and what numbers they were in previous NEC editions. If you can view Excel files, you can download a copy of it here.
 
Last edited:

readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
I also see many subpanels with neutral and ground on same bar, enforcement is the difference, until late 90's we did not have county inspections, some think that rules changed in cases where rule hadn't changed, enforcement changed.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
1968 contained a new article, 384-27. It is now 408.20.

I have compiled a database of certain Code references and what numbers they were in previous NEC editions. If you can view Excel files, you can download a copy of it here.

408.20 ???? Location of switchboards??
 