OUTLET BOXES SUPPOTRTED TO CABLE 2008 NEC
grumpy11
WE ARE DOING AND IT ROOM WE INDEPENDLEY SUPPORTED THE OUTLET BOXES AND NOT SUPPORTED THEM TO THE CABLE TRAY. THE DOES CODE PERMITT BOXES TO BE SUPPORTED TO CABLE TRAY
I come up with art.392.10. Cable trays shall be permitted to be used as a support for service conductors, feeders, branch circuits, communication circuits control and signal circuits. I don't see boxes as being supported by the tray but I will defer to others.
Oh and please don't use all caps.
i believe thats 392.3 (Per the OP’s 2008 request)
OULTET BOXES SUPPORTED TO CABLE TRAY 2008 NEC
i agree but it doesnt say that a box can be supported to cable tray.
sorry for caps. before
What does this mean:For boxes and conduit bodies attached to the bottom or side of a cable tray system, fastening and supporting shall be in accordance with the requirements of 314.23
but 392.6{j} is for industrial facilities.
my installation is in an office buliding for an IT room
Then the permissible part doesn?t apply to you. :D. So, no you can?t attach it per code. This applies to industrial non-commercial>>>unless your jurisdiction says otherwise.
392.6 {j} seems to be the only referance to mounting outlet boxes to a cable tray.
but only in industrial facilities.
so i would say no you cant unless the AHJ tells me other wise.
Note: That is what I posted, and said. Are you talking to yourself:lol: