Anyway,  see  my post#  104,  Bes.  Perhaps  the  study  of  destruction SPD with parallel mov's is not complete till date. You may have a chance to enhance the knowledge of humanity about this particular mode of failure by following my suggestion in that post. Hope you may mention me somewhere in your report........
I've never seen
a solid state device fail owing to mechanical force.
Singular. That's where the topic started.
You moved the goalposts to include an array of such devices to try to support your contention.
But, let?s look at a few simple numbers to see if it does.
You are no doubt conversant with the definition of the Amp?re as the constant current that will produce an attractive force of 2 ? 10^7 newton per metre of length between two straight, parallel conductors of infinite length and negligible circular cross section placed one metre apart in a vacuum.
That gives us a starting point. Let?s assume that the fault current is 10kA. We have something under that from the supply in our test bay so maybe not an unreasonable assumption. How far apart are the MOVs? Say 20mm (about ? of an inch). Chuck those numbers into the Besoeker blender and you come up with a force of 5N. With me so far?
So what is a force of 5N like? One newton gives a mass of one kg an acceleration of one m/s/s. If the MOVs weigh just 0.1 kg then acceleration would be 50m/s/s
For time, let?s take a generous 20us.
We can now apply Newton?s laws of motion. Specifically that for distance.
s = ut + ? at^2.
Initial velocity, u, is zero.
So, we get s = 0.00001mm.
I think the numbers simply don?t support your contention.