The typical 12kW electric range requires a 50 ampere circuit when operated on the common residential 240 VAC. However, many condos, apartments, and cluster homes are fed 120/208 VAC derived from a three-phase transformer bank. I know of several cases where a resident purchased a 240 VAC-rated electric stove, clothes dryer, or water heater from an appliance store and was disappointed in its lackluster performance. Further investigation revealed that the resident lived in a facility that had 120/208 VAC power. In each case, the resident was unaware of the available voltage, and the appliance salesperson never asked about it. Ohms Law will prove that a resistive heating appliance rated for 240 VAC will produce only 75% of its capacity when operated at 208 VAC.
My concern is that some appliance manfufacturers do make 208 VAC-rated ranges, but a 12kW range at 208 VAC will require a 60-ampere circuit. The NEC does not acknowledge this fact, and I submit that this is a significant oversight that needs to be corrected. Likewise, electric clothes dryers and electric water heaters intended for 208 VAC operation will require higher-rated circuits to handle the higher currents. I don't think the average appliance buyer is aware of the practical implications of a 208 VAC service.
My concern is that some appliance manfufacturers do make 208 VAC-rated ranges, but a 12kW range at 208 VAC will require a 60-ampere circuit. The NEC does not acknowledge this fact, and I submit that this is a significant oversight that needs to be corrected. Likewise, electric clothes dryers and electric water heaters intended for 208 VAC operation will require higher-rated circuits to handle the higher currents. I don't think the average appliance buyer is aware of the practical implications of a 208 VAC service.