I am not using the wrong formula, you are misunderstanding the OP's point. Reread his posts #1 & #8.
He is decrying the fact that a 12000W/240V range will under-perform on a 208V circuit. He further suggests that one can install a 12kW/208V rated range. The 12kW/208V range on a 208V circuit will have a higher load current (57.7A) than the 12kW/240V range on a 240V circuit (50A.)
I agree. The OP gets the math. I think he is saying the same thing I said in post #13. It is an annoyance to some customers who are serious cooks. I've even had customers who say they have the exact same range, etc at their other home "up north" and want to know what is wrong. When try to explain this to the owner of a very expensive condo, they think it is lame.