Microwatt

Senior Member
Location
North Dakota
Installation of a counter top water/ice machine. Nameplate says min ckt ampacity 19.3 amps, max OCPD 25 amps. There is a J-box on the back of it for the attachment of a cord or other wiring method. Since it needs water it is located with-in 6 feet of a sink. There is already a 20 amp GFCI receptacle in place fed by a dedicated 20 amp breaker.

Is it legal to put 12/3 cord with a 20 amp plug on this machine and plug it into the GFCI receptacle?

Also, is a typical GFCI receptacle considred a single receptacle or is a duplex?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A gfci receptacle is a duplex receptacle not a single receptacle according to art. 100 definition of receptacle.

If you connect this to a 25 amp circuit how will you connect it to a 15 or 20 amp recep. Look at 210.21(B)(2)

If you direct wire it then you will not need gfci protection.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It has been argued herte previously, but, the fact that your duplex GFCI is considered to be (2) outlets by most, then 210.21(B)(2) would not allow the 19.3 amp load.
If you protect a single outlet with a GFCI device, you could use that since the 25 amp is maximum.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It has been argued herte previously, but, the fact that your duplex GFCI is considered to be (2) outlets by most, then 210.21(B)(2) would not allow the 19.3 amp load.
If you protect a single outlet with a GFCI device, you could use that since the 25 amp is maximum.
How can you use a 25 amp breaker on a 20 amp device? I would not suggest using a 20 amp OCPD
 

renosteinke

Senior Member
Location
NE Arkansas
I would submit that the usual 'ampacity' rules do not apply here.

Rather, an ice machine, or even a refrigerator, is akin to an air conditioner, and air conditioner rules apply.

Most notably, the effect is that you have a much larger OCPD than the 'usual,' and you get to run smaller wire.

Nor would I consider this a 'continuous load.'

19.3 FLA is well within the 25 amps allowed #12 wire. The "*" in the ampacity table leads you to the code sections that explain this.

19.3-A is also within the limits of a 20-A device.

Breakers and devices are not sized for each other; they're sized for the loads. In this case, both are compliant.
 

Microwatt

Senior Member
Location
North Dakota
Thanks for the replies. I was thinking it either has to be a 20 amp GFCI breaker to a 20 amp single receptacle via #12 wire. Might not be the best but I think it would be legal. Or, 30 amp receptacle fed by a 25 amp breaker via #10 wire. No GFCI protection provided with this option. Just to clairify, this is a 120 volt circuit.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If you use a 25 amp breaker, there is no code reason to use a conductor larger than #12 for this application. In my opinion this equipment is within the scope of Article 440.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
How can you use a 25 amp breaker on a 20 amp device? I would not suggest using a 20 amp OCPD

i did not make myself clear, apparently. He could, IMHO, use a 20 amp single outlet protected by a GFCI device (breaker, dead-front, etc). I only mention3d the 25 amp as it is maximum but not permissible on his 20 amp receptacle.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If you use a 25 amp breaker, there is no code reason to use a conductor larger than #12 for this application. In my opinion this equipment is within the scope of Article 440.

I agree. However, he could not use the 20 amp receptacle, correct ?
 

hurk27

Senior Member
I think if you use a receptacle your not going to get around 210.21(B)(1)
B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit
.

Is this a dwelling or commercial?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Is there any condition where a 25 amp OCPD can be protecting a 20 amp receptacle?

This is something I've always wrestled with. I don't think there is any condition where this is allowed. This often comes up with a motor load that is cord and plug connected.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is something I've always wrestled with. I don't think there is any condition where this is allowed. This often comes up with a motor load that is cord and plug connected.

I agree. So he's either stuck with a 20 amp receptacle and a 20 amp OCPD or a 30 amp receptacle and a 25 amp OCPD.
 

hurk27

Senior Member
I don't see any allowance for a 20 amp receptacle to serve a 19.2 amp load, Table 210.21(B)(2) only allows a 16 amp load on a 20 amp receptacle, But I don't see anything that prevents a 30 amp receptacle on a 20 amp circuit, personly I would go with hard wired.
 