And another good reason to have individual PFC upstream of motor protection devices.RaiderUM...
Another Caveat if you chose to apply PFC to individual motor loads: Don't forget to adjust any thermal overload device for line-current reduction!
Phil
And another good reason to have individual PFC upstream of motor protection devices.RaiderUM...
Another Caveat if you chose to apply PFC to individual motor loads: Don't forget to adjust any thermal overload device for line-current reduction!
Phil
Besoeker
Do you not believe me???
Phil
Were you talking about a complete unit including the motor or just the motor alone?Besoeker
Do you not believe me???
Phil
According to the demand and PF you posted you need a total of 5000 kvar to get the PF to 0.96. If these caps
were off line during billing, then they should be online and that would leave you 3800 kvar additional to add.
Disbeliever in what? I'm fact-finding. You mentioned data from a compressor-drive and I was not sure what was included.Mivey...
Are you a disbeliever as well?
OKRegarding your "motor alone" question; the motor alone, of course.
No expectations. Just had a simple question.Did you expect a shaft-coupled wound-rotor starting-motor, too?
I took time back-reading and really believe your problem is about finding the best setup that allows your BAS to respond to whatever load PF you will be experiencing for a wide range seasons! Without knowing how your building automation system is capable of (does it initiate 'raise' or 'lower' signal to your PFC controls, are these power factor devices operate on its own, etc.), it would be best to tabulate each of your building loads and it's PFs and start your analysis from there.
My own experience with a 900 kVAr, 12-step, automatic power factor control on a multi-function rooms convention center gave me headaches as under and over-correction always occurred when the building was first used. I managed to solve the frequent capacitor contactors hunting when I tweaked the amount of kVAr that can be switched-in at different PFs caused by HVAC cycling. It was a 75 kVAr per step but that setup led to over/under correction. We have to lump more caps on one bank than the others while some were made to cut-in less than 75 kVArs.
Hope that helps you.
See post #54.
I don't know if I explained it very well.
As it happens, I was a question I was asked on site today.
I've spent the last three days on site with my guys getting a couple of 3,000HP, 11,000V variable speed fan drives back up and running after a major supply problem had taken out much of the electronics.
Centrifugal fans have a cube law curve for power. Double the speed, eight times the power. (2^3)
So, at half rated speed, the motor ought to be at one eighth of rated power.
In this case, the speed range is from half speed to full speed. Ought to be under 400kW at minimum speed.
One guy, a sharp cookie from the customer's side asked why the stator current was still relatively high at such a relatively light load.
The answer is simply that the power factor is so much worse on lighter loads.
RaiderUM...
Another Caveat if you chose to apply PFC to individual motor loads: Don't forget to adjust any thermal overload device for line-current reduction!
Phil
I'm not sure quite what you mean.Beseoker...
By "upstream" do you mean upstream of the OL, but downstream of the contactor?
Phil
Just the data recorded at the FAT would be fine rather than anything developed from it.Beseoker...
You too should know nameplate does not list no-load curent! However, if you also want proof of its size would a copy of the manufacturer's circle diagram, developed from FAT, suffice?
Of course it varies.
I was simply pointing out that your suggested15% was rather atypical of no load kVA.
Besoeker...
Tit-For-Tat, huh :happyyes:
How about an 11,400 kW (15,300 Hp) ethelene compressor-drive, having a no-load current of 135A and a full-load current of 750A. NL/FL ratio is 18%. Closer to 15% than 30%.
Regards, Phil
Don't really think so.Y'all:
Care to read faithfully what you both have posted? You could be talking about the same thing, IMO.
Bes said "15% was rather atypical of no-load kVA" while Phil said "having a no-load current of 135A and a full-load of 750A"! Anybody can reconcile no-load kVA with No-load current! Discussions may be put to rest right there.
Besoeker...
The curves you expect fromthe mfgr will not reveal the I values. So I ask again, "... do you want corroborating documentation?"
Phil
Not a lot which is why I took issue with the 15%Bes & Phil,
So we are getting to around 20% with these big 1,000's of HP motors (kW for Bes). How applicable do you think that is to the OP's 100's of HP?