No disagreement with your calculations at 720kVA.
But you might need also to consider minimum kVA to avoid the possibility of over correcting and getting a leading power factor.
That is why he is proposing to use an automatic power factor correction arrangement. I think you did not read the thread in full.
Besoeker, Thank you for confirming!
We do not get charged for a Leading PF. Which is why I am leaning toward Fixed banks and putting Caps on the Load side of the Chillers Starters for cost reasons.