czars
Czars
- Location
- West Melbourne, FL
- Occupation
- Florida Certified Electrical Contractor
Can anyone explain how the enphase micro inverter interacts with the utility? Does the output stop when the utility disappears?
The simple (not necessarily accurateCan anyone explain how the enphase micro inverter interacts with the utility? Does the output stop when the utility disappears?
Yes, it shuts down when the grid goes down or is disconnected. It has to be that way for several reasons, only one of which is that it is required by law.Can anyone explain how the enphase micro inverter interacts with the utility? Does the output stop when the utility disappears?
I found some info on the Enphase site about the criteria for disconnecting from the utility. However I could not find anything about the connecting criteria except a reference to a 5 minute wait. Anyone have more info on the connecting criteria?
Enphase M215s (and D380s) are a little unusual in that they are designed to operate in both 240V and 208V systems. I'm not sure if the inverter knows which is which; it may only shut down if voltage falls outside the range for both types of systems.
The simple (not necessarily accurate) explanation is the inverter measures the voltage level required to "push" its current onto the connected system (utility or otherwise). When the utility power is disrupted, it takes less "push". At a preset threshold, the inverter disconnects its output. Required for grid-tie inverters.
As I thought about this a little more it occured to me that the inverter can probably calculate the ratio of the line-line and line-neutral voltages to tell if it is on a single phase or 3-phase supply, then look for the appropriate voltage range.
How so?... and where's your "better" explanation.That's simple, and wrong.
Enphase MIs sense the line voltage and compare that against the valid ranges. They don't have access to all three phases, just two lines which may or may not be the same phase (for 240 volts systems).
Remember that the maximum range for system voltage is +/- 10% of the nominal value. So, for 120/208 systems, line-to-line is in the range 188 to 228 (more or less) and for 120/240 single phase, the range is 216 to 264. While there is 12 volts of overlap (from 216 to 228), that's not a whole lot of the total range (188 to 264).
It's a pretty stupid-simple thing to figure out, provided the power electronics and inverter firmware are up to the task.
While there is 12 volts of overlap (from 216 to 228), that's not a whole lot of the total range (188 to 264).
At an Enphase training session a few years ago it was explained that the inverter measures the voltage with respect to the neutral and does not measure voltage line to line. To determine if the inverter is on two legs of 3-phase 120/208, the inverter measures the phase angle and sets the voltage limits accordingly.
Correct me if I'm wrong, but don't these inverters only connect L-L? So I'm wondering how a L-N measurement is possible. With no direct neutral connection, perhaps they use the EGC for reference...???There you go, thanks Bill. Of course measuring phase angle is another option.
The only thing that's a loose end with me with this is that inverters report voltages to Enlighten that are e.g. 220. I wonder if they just multiply by 2. In that case the voltage measurement may be a little inaccurate.
4 conductors: Line 1, Line 2, Neutral, Ground.Correct me if I'm wrong, but don't these inverters only connect L-L? So I'm wondering how a L-N measurement is possible. With no direct neutral connection, perhaps they use the EGC for reference...???
Why would they do that if they could combine the 120 V voltage vectors? FWIW, traditional utility residential meters meter Line-Line and thus have slight metering errors when the voltage is unbalanced.There you go, thanks Bill. Of course measuring phase angle is another option.
The only thing that's a loose end with me with this is that inverters report voltages to Enlighten that are e.g. 220. I wonder if they just multiply by 2. In that case the voltage measurement may be a little inaccurate.
They would not need access to all three. With access to the grounded conductor, you can measure the phase angle differences between the 120 volt signals with a neutral reference. A 120/240 system will show 180? difference and a 120/208 system will show a 120? difference. THEN it is stupid-simple.They don't have access to all three phases, just two lines which may or may not be the same phase (for 240 volts systems).
She really did not say anything. The basic test is voltage and frequency. These are not adequate by themselves and there are many other tests that can be added. Many inject a small signal distortion (like a frequency shift, etc) and check to see if the response is dominated by the inverter or something else (the grid). You can even go so far as to have the grid send a SCADA signal to let the inverter know the system has tripped but that is probably beyond the scope of what you would do with MIs.How so?... and where's your "better" explanation.It seems to me, you're saying the same thing with different words...
I see... and additionally Line 3 for 3? system connection.4 conductors: Line 1, Line 2, Neutral, Ground.Correct me if I'm wrong, but don't these inverters only connect L-L? So I'm wondering how a L-N measurement is possible. With no direct neutral connection, perhaps they use the EGC for reference...???
First, mislead to believe connected only to two lines...They would not need access to all three. With access to the grounded conductor, you can measure the phase angle differences between the 120 volt signals with a neutral reference. A 120/240 system will show 180? difference and a 120/208 system will show a 120? difference. THEN it is stupid-simple.tallgirl said:They don't have access to all three phases, just two lines which may or may not be the same phase (for 240 volts systems).
What do you mean? She said my "simple" explanation in post#2 was "wrong", with nothing presented to explain her comment. Let's experiment... you are wrong?She really did not say anything. ...