ggunn
- Austin, TX, USA
- Consulting Electrical Engineer - Photovoltaic Systems
I'll take a swing at this one. PV inverters are current sources*, and as such do not need to have a higher voltage output than the grid to "push" energy onto it. Yes, there is voltage drop between the inverter and the service resulting in a voltage rise at the terminals of the inverter, but the magnitude of this rise does not determine the amount of power output. You could, for example, run a parallel set of conductors from the inverter to the service and thus cut the voltage rise in half and the power output from the inverter would remain unaffected. You could theoretically run a superconductor line from the inverter to the service and reduce the voltage rise to zero, and the inverter would still export power.What do you mean? She said my "simple" explanation in post#2 was "wrong", with nothing presented to explain her comment. Let's experiment... you are wrong?
* Since the output voltage of the inverter is clamped by the grid voltage, that makes it in reality a current source at constant voltage - a power source.