If a ds circuit breaker has a ka rating of 85,000 scca can the digatrip lower the ka rating of the ds or dsl breaker ?
If you were to use the70e tables and the cb was rated outside the notes can one say the trip unit was a way to lower the scca and were able to use the table.
Yep, two totally different issues.The tables have limits on available fault current, not the breakers AIC rating.
My manager told us to dress at level 4 ppe because working on equipment was a hrc4 according to the tables . Now [our equipment]the bus has 100,000scca rating the cb has 85,000 scca [as posted on equipment label]. Maybe i am wrong but the tables list 35,000 scca limits[ for the tasks] and if our cb is rated for 85,000 it sounds like we are operating out side the parameters.
You can't, simple as that.Now how can someone use the tables if they don't know the parameters of the system?.
The contractors have to follow the same rules as you.Also told manager about working energized but it did not seem to matter, his answer was to use contractors.
You have made it clear many times your manager is a tool.I come across to him as not being a team player, when i am trying to do the work safe.
Now [our equipment]the bus has 100,000scca rating the cb has 85,000 scca [as posted on equipment label]. Maybe i am wrong but the tables list 35,000 scca limits[ for the tasks] and if our cb is rated for 85,000 it sounds like we are operating out side the parameters. Now how can someone use the tables if they don't know the parameters of the system?. I was using the breakers label listing , which you guys say is wrong.
The listings on the labels have only to do with what the breaker CAN withstand, it has nothing whatsoever to do with what EXISTS in the system. You can ASSUME, at best, that whoever selected the equipment did so based on the Available Fault Current being LESS that the ratings of the devices, but that could be ANY amount less. So if all you are looking at is the fact that you have a breaker rated for 85kAIC, that is not telling you anything useful with regards to the PPE requirements. If the guy who is responsible says use PPE4, you have to use PPE4.
I guess it was a poor choice of words on my part, I should know better. I meant "Interrupt", but I was mainly trying to get the message across that the label on the breaker is not meant to indicate the AVAILABLE fault current in the system.It has to be noted that the KAIC rating of a breaker is pretty much what it's withstand rating may be. I'm not aware of a breaker having a withstand rating other than it would be basically what it's (kaic) interupting rating is. Isn't the withstand rating commonly limited to non-automatic devices?
I know breakers need to interupt should they experience anything close to what their withstand rating may be to protect themselves. As such withstand ratings for a breaker is not of much value.