billdozier 78
- Orlando
Had to size a 70 amp load today. Knew the breaker had 75 degree terminals so sized per that table. My question is when does the 90 degree column come into play?
Thanks for the reply. Let me take this one step further to make sure I grasp it. Lets say we had a 100 amp load and 7 current carrying conductors in a conduit. A #3 wire in 90 degrees is good for 110 amps. But I have to multiply that 110 amps by 70%. That would be 77 amps. I would run a #1 to carry that load since #1 equals 150 amps less the 45 amps of heat dissipation. How far off am I?
You are close, but you can also apply 240.4 (B) and run #2's. See also 240.6 for standard breaker sizes. Otherwise, your premise is correct.
The OP needs a one hundred amp conductor so I believe he got it correct. #2 at 90C 130 amps but at 70% it is 91 amps and although the breaker can be sized at 100 amps the load cannot be greater than 91.
210.19 Conductors ? Minimum Ampacity and Size. (A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.