Being an "emergency" temporary situation, he likely doesn't have a buck transformer handy. If the transformer has voltage taps, could he use two primary windings to develop <120-N ? 2, >208 L-L, but close enough secondary voltage?No.
You can use use any transformer arrangement to go from 1-phase to 120/208. To get this voltage you need a 120? phase shift.
Do you need really 208V L-L? Can you use a standard 120/240V arrangment and then 'buck' the 240V to 208V?
The OP said 480 delta 3? transformer.The OP said single phase primary. There is no way to get 208V from the output of wye connected transformer windings, if you only feed them with single phase.
craigo321 said:Can I make a 3 phase delta (480V) transformer work...
Read the entire OP.The OP said 480 delta 3? transformer.
Connecting 480V 1? to two windings of a delta-wye 3? transformer is a single phase primary.Read the entire OP.
It said 3-phase transformer and single phase primary.
My assumption as well.My assumption is they have lost their 3-phase supply for a period of time, and would like to continue to supply the existing 120V and 208V equipment.
I'm not saying the connection I suggest will replicate 120/208V 1? 3W.The answer is no, you cannot replicated the 120V and 208V relationships with only a single phase primary.
I know. You suggested 120/240V 1? 3W (with a buck transformer). Just how do you propose to get that 120/240 from a 480D:208Y/120 3? transformer? Wouldn't you have to connect 480V 1? to two primary windings? So you'd get 120/240V 1? 3W off the two mating secondary windings. Correct?A standard 3-phase delta-wye transformer has fixed winding interconnections, so the possible output voltages are limited.
Okay, here's a typical 480 to 208/120 transformer connection diagram...Connecting 480V 1? to two windings of a delta-wye 3? transformer is a single phase primary....
What I'm saying is if the primary has voltage taps (i.e. they are usually on the primary), connect to the highest voltage taps so it reduces the secondary voltage to something below nominal for L-N, and the L-L voltage will double that... it will be higher than the nominal 208, but both voltages (L-N and L-L) would be within acceptable tolerances.
Connect to two primary windings, 480V each.Connecting the single phase 480V across two primary windings will result in in the windings being in parallel this will mean each winding sees 50% of the input voltage so the output will also be only 50%.
Please examine the following diagram carefully...If you connect two of the windings in parallel (i.e. jumper C->B, and then feed 480V to A and B/C) you will get about 120V from two of the secondary windings. However, because you have changed the intended relationship between the primary H1-H2-H3 and X1-X2-X3 terminals the (2) resultant 120V outputs will not combine to create 240V.