250.64(C) does not apply to installations that have multiple service disconnects. 250.64(D) applies to services with multiple disconnects and the code section clearly calls the conductor that is run from the GEC to the service disconnects a "grounding electrode conductor tap". The section clearly permits any connector listed for grounding and bonding to be used to connect the grounding electrode taps to the grounding electrode conductor. The grounding electrode conductor must remain unspliced. There is no requirement that the grounding electrode conductor be run to one of the disconnects.
OK it only needs to be continuous till it ends! :?
So what does all this mean?
(2) Individual Grounding Electrode Conductors. A
grounding electrode conductor shall be connected between
the grounded conductor in each service equipment disconnecting
means enclosure and the grounding electrode system.
Each grounding electrode conductor shall be sized in
accordance with 250.66 based on the service-entrance conductor(
s) supplying the individual service disconnecting
means.
(3) Common Location. A grounding electrode conductor
shall be connected to the grounded service conductor(s) in
a wireway or other accessible enclosure on the supply side
of the service disconnecting means. The connection shall
be made with exothermic welding or a connector listed as
grounding and bonding equipment. The grounding electrode
conductor shall be sized in accordance with 250.66
based on the service-entrance conductor(s) at the common
location where the connection is made.