Prior to the 93 code the "full size" EGC rule only applied to parallel conductors in raceways.   The panel statement on the proposal to make this rule also apply to parallel cable installations said.
There were no comments in the TCD (now know as the ROC) on this proposed change.
So, you maintain that there is no difference between cables and raceways (as far as code issues concerning internal EGCs)
Well, here is a similar question:
Most of the mc-hl comes with 3 paralleled, internal, insulated grounding conductors.  That would never be allowed in RMC.  Do you wish to never use MC-HL for that reason?  In your words, if it is unsafe in RMC then it is unsafe in MC.  If you wish to be consistent, you should be arguing to ban any MC cable with segragated grounding conductors.
Or, more probable, the panel didn't mean that cables and raceways should be treated equal in all respects.  Since you brought it up, let's look at NEC 1996.  .
1996 250.95 is where the "or cable(s) was added.  Thei section is the "size of equipment grounding conductors".  This section references 1996 250.91.b, types of equipment grounding conductors:
The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
(8) The metalic sheath or combined metalic sheath and grounding conductors of type MC cable.
Regardless of the what was in the TDC, what made it into the code sounds pretty clear to me.  In 1996 the Code allowed the use of the combined sheath and internal egcs.   And the section on paralleled conductors referenced that.
Fast forward to 2011:  2011 250.122.F specifies the size of the equipment grounding conductor.  2011 250.118.10.c specifies what can constitute an egc.  And the combined sheath and internal grounding conductors are specified as a equipment grounding conductor for certain types of MC cable.
Paraphreased:
You say there is no science or physics that says cable should be treated different than conduit.  And I mostly agree, and remind you that regardless, the code does treat them differently.
You say there are no documents that say it is okay for paralleled MC cables to use the combined sheath and internal egcs.  And I say 250.118.10.c specifies what constitutes an ecg.  And, the NEC is permissive - Show me a document that says you can't.
This has been repeated unto near nausea times.  Saying it more often or louder makes neither side more true.  It's time to move on.
Here's my suggestion:  One more apiece (on this subject anyway, plenty of others this could morph into.) - with something different from the above two.  I'll keep mine short.
ice