ElectricPersonality
 - Philadelphia, PA
If you get a calculated wire size of 413 amps from your Combiner box output circuit (panel short circuit current x 156% x the number of strings connected to combiner) to the inverter, would it stand to reason that the combiner box bus size would need to be greater than or equal to 404 amps?  Is there any exception in the code that would allow you to use a 400 amp combiner box?  Article 690 doesn't specifically talk about combiner boxes as it relates to ampacity size.