Find the power company transformer. Run a long test lead from the ground rod at the transformer. You might measure the current in the transformer grounding wire. It should not be very much. This wire will be a moderately heavy wire relative to expected normal current, and whatever current is in the wire won't produce much voltage drop from the transformer center tap to the ground rod. If there is high current, then you know there is some kind of problem.
One thing to keep in mind is that, if you are dealing with a broken or weak neutral, it can be broken or weak before or after the utility transformer. Either way you can measure current on the transformer ground wire and there can be shocks felt on the property. Gar's next step will help determine where that break or weakness is.
This test lead is taken to the main panel. Note: there could be a large voltage between the test lead wire and the main panel neutral. Be careful and use suitable equipment.
Measure the voltage difference between the main panel neutral bus and the transformer ground rod. This is the voltage drop across the transformer neutral to main panel neutral, assuming not much voltage drop on the transformer grounding conductor. If the first experiments with the light bulbs or meters did not indicate a large voltage change with normal load changes, then while monitoring the neutral path voltage connect a 100 W load to one phase. Note: the change in neutral voltage difference. At 8 A at my home I get about 0.2 V change. At 200 A this would extrapolate to about 5 V. If with the 100 W load you get a very small change, then try a 1500 heater, about 12 A.
Note: my calculated neutral path resistance is about 0.2/8 = 0.025 ohms.
.
At this point you will have enough information to determine whether this is a bad neutral, and whether it's before or after the utility transformer since you've effectively checked the neutral from the service back to the transformer. If the current and voltage readings are similar when taken to the neutral or the test lead and a neutral symptom still exists, then the break is on the primary side of the transformer (In those areas of the country where single phase 120/240 is derived from a primary phase and neutral...).
Reading the OP, it seems to me that calculating all this would really only help if the broken or weak neutral is between the service and transformer. Otherwise, with neutral current returning from the transformer back through the utility grounds the variations in soil conditions (mineral content, moisture level, breakage point in the network etc.) could hugely affect any calculations by introducing an enormous number of unknowns.