ERIC LEDBETTER
Member
I was contracted by a local mechanical contractor to bring power to a 125 amp libert ac unit at 480 volts . They made a mistake and ordered a 208/240 at 155.5 amps unit at a coast of 50,000 returning it is not an option . SO I set a 45k 208 volt transformer. on start up the ac is at 211 volts (nice) however the commissioning of the unit requires the ac and DE humidifier and heating element to run at the same time as the ac this is causing the voltage to drop to 198volts He still has more items that need powered at the same time and my fear is he will lose even more voltage..
Any suggestions before i get back to this guy Monday morning .