- Location
- Illinois
- Occupation
- retired electrician
What is the voltage on the primary side of the transformer when it is loaded?We installed a 75 k but phase a under load only puts out 198 volts not 208 . trace it out further the 277 primary from street only has 274 on phase a. is it worth up sizing this thing again at the expense of the H V A C guy. without a load we run only 201 one a 205 on b and c the primary run is less than 110 feet and the wire is over sized . Looking for help