One more transformer protection quesiton for the day
I'm looking at an appliation where there is a 45kVA transformer 480V-pri, 208V-sec. Primary breaker is an 80A breaker and secondary main breaker in panel on secondary is a 200A breaker. From what I see the secondary 200A breaker does not provide adequate secondary protection of the transformer.
Since the 80A primary breaker is larger than 125% of the transformers primary rated current then secondary protection is required for the transformer. The required secondary protection can be a maximum of 125% of the transformers secondary rated current. 125% of this transformers secondary rated current is 156A (125A * 125%). The 200A secondary breaker exceeds this 156A value and therefore does not provide adequate required secondary protection.
My recommendation would be to change the 80A primary breaker to a 75A breaker which will be within 125% of the transformers primary rated current and therefore no secondary protection will be required per 450.3(B). Do others agree that if primary breaker is within 125% or primary rated current than no secondary protection is required?