If the OCPD on the secondary side does not exceed 125% of transformer full load current for the condition stated in post#79, it can be considered that the transformer is protected.If the secondary conductors are 3m or less you can use (C)(2) to protect them instead of the primaries. Note that (C)(2) protects the secondary conductors without using OCPD. Example: 240.21(C)(2)(1)b mentions the poster's 200A OCPD as "the overcurrent-protective device at the termination of the secondary conductors." Here they've avoided calling the OCPD at the far end of the run "Secondary OCPD" because it's not being used for the transformer protection.