The constant voltage transformer should fix the issue with my equipment. Is there a legitimate concern every other piece of equipment is subject to the same harm from low and unbalanced loads this building is full of servers and Air conditioners. A spot check showed the same A phase under powered. This building (Tela Pacific) is quick to point out 12.5 million a day if power is lost
A line to line voltage imbalance exceeding 1% can cause motor losses, heating, to go up 25%. If the line to line voltages are exactly equal, motors can tolerate more +- % line voltage.
If the line to line voltage imbalance exceeds 1% regularly, you say the A phase has a lower voltage, file a voltage complaint with the utility. They may come out and put a data logger on it and are likely required by law to fix something out of spec.
The servers are usually multivoltage power supplies and tolerate a wide range. Voltage fluctuations and imbalances on the motors will throw the motor efficiency off by enough to cause some problem.
Should add a note about the transformer taps. Do not change only one tap to correct lower voltage on one line, each phase has to be tapped equally, the same. Line to line voltage imbalance at the utility is a utility problem.