T
T.M.Haja Sahib
Guest
Even when there is a output filter?The physical design deliberately ensures that impedance between the bucket and the IGBT switching elements is negligible for entirely practical reasons.
Unnecessary complication and equivocation.Even when there is a output filter?
I only wanted to stress that the presence of output filter implies that the leads from AFD output are long and so their impedance is not negligible.Unnecessary complication and equivocation.
What happens at t>0?
That's a different scenario.I only wanted to stress that the presence of output filter implies that the leads from AFD output are long and so their impedance is not negligible.
It doesn't. The capacitor on the LHS, C1, is the DC bucket so will be at the voltage of the rectified AC. Possibly around 600Vdc. Until you close SW1, C2 would most likely be uncharged.If you say the impedance between the capacitors is negligible, the voltage difference between the two capacitors should also be negligible. This follows from Kirchoff's voltage law.
The mistake is not in terms of design. It would be in connecting a capacitor across the output terminals of the inverter which is why I wrote, all those posts ago, that doing such a thing is an absolute no no and maybe, just maybe, you are now beginning to understand why.But if you still insist that the voltage difference is not negligible, it means that you committed a design mistake by choosing wrong size capacitors and so do not close that switch; heavy current would flow.
I despair.I am willing to learn from you too. But do not be evasive. Consider this: high dv/dt from AFD could cause damage to the driven motor winding but a capacitor across its terminals can smooth it out safely.
The basic building blocks diagram of ASD is given at page 8 of link below and note presence of capacitor on the output side of ASD for function I already mentioned.I despair.
You can't do that. It is an absolute no no.
You will notice that this filter does not result in a capacitor in parallel with a capacitor. You may also note from page 16:The basic building blocks diagram of ASD is given at page 8 of link below and note presence of capacitor on the output side of ASD for function I already mentioned.
http://pes-psrc.org/Reports/Final_J...plication_and_Issues_Working_Group_Report.pdf
3. If there are capacitors on the bus feeding the ASD, such as power factor correction capacitors, resonances can occur which can be damaging to electrical equipment on the system. Capacitors located between the drive output and the motor terminals should be avoided.
it is the high harmonic content in the output of VFD that does not permit use of any capacitor on the output side.
Consider this: high dv/dt from AFD could cause damage to the driven motor winding but a capacitor across its terminals can smooth it out safely. But owing to high harmonic content, use of capacitor on the output side of AFD would damage it. My plan is to use a filter to take care of harmonics so that the capacitor could be used to reduce the dv/dt to a suitable value across the driven motor terminals.......
It seems like you have said more than one thing, but I may have missed a post or two. Do you have a diagram of what you plan to insert between the drive output and the motor?Agreed. But my point is this
And, as I already mentioned in post #84, that is a different scenario. In Fig. 2, The capacitor is NOT connected to the output side of the variable frequency inverter.
And I keep telling you that can't do that.
I never told you it could be done. I am afraid you misunderstood.I keep telling you that can't do that.
It absolutely is the high dv/dt.It is better to start another thread to discuss further because it is neither above nor high dv/dt that causes failure but it is the high harmonic content in the output of VFD that does not permit use of any capacitor on the output side.
Here is what you posted;I never told you it could be done. I am afraid you misunderstood.
That seems to at least suggest it could be done without detriment.The current would, of course, rise. But if the switching is very fast as in IGBT, the rise in current may not be too high to blow a fuse.
Try it and report back.If you give your remark on the suggestion in post#93, it would be nice.