Where does the table give you leeway to ignore the presence of the secondary OCPD in order to use row 1? This is NOT a "Primary only protection" installation. There IS a secondary.
The OCPD on the secondary side which is providing protection to the secondary conductors is not relevant to the TRANSFORMER protection.  The Table is titled "Maximum Rating or Setting of Overcurrent Protection for
TRANSFORMERS 600V and less (as a Percentage of
Transformer-Rated Current)"
The table is referenced in section 450.3, which says: "Overcurrent protection of
TRANSFORMERS shall comply with..."
Table 450.3(B) only tells us what the requirements for protecting the
TRANSFORMER are.
The Table gives you two
Methods for protecting the
Transformer (see the left most column):
.....Method 1: "Primary Only Protection"
.....Method 2: "Primary and Secondary Protection"
For Method 1, the Maximum Rating of the Primary OCPD can be 125% of the primary rated current (or next size up.)  If the primary OCPD meets this maximum rating, then no secondary protection is
required, and you have a "
Primary Only" protected transformer.
If the Primary OCPD is greater than 125% (or next size up), such as the 80A primary OCPD in the OP, then you must look at the second method.  For method 2, the Maximum Rating of the Primary OCPD can be 250% of the primary rated current.  In this case, the Secondary OCPD can have a Maximum Rating of 125% of the secondary rated current (or next size up), and you have a "
Primary and Secondary" protected transformer.
In the case of the OP, the Primary OCPD (80A) exceeded the allowable 125% (or next size up) for the "Primary Only" method, BUT the secondary also exceeded the allowable 125% (or next size up) required for the Secondary Protection in the "Primary and Secondary" method, so the installation was non-compliant with 450.3(B).
There are two options to correct the non-compliance.  Make the transformer protection comply with Method 1 "Primary Only", or comply with Method 2 "Primary and Secondary" protection.
Reducing the Secondary OCPD to 175A would make the installation comply with Method 2.  The primary OCPD would still be greater than 125%, but less than 250%, and the Secondary OCPD would be less than 125%.  Therefore, the Requirements for
TRANSFORMER protection in T450.3(B) would be met, and assuming the primary and secondary conductors were already properly protected by the 80A and 200A OCPDs, reducing the secondary OCPD to 175A, the
CONDUCTORS will still be properly protected per 240.4 & 240.21(C).
Reducing the Primary OCPD to 70A would make the installation comply with Method 1.  The primary OCPD would be at 125% (or next size up) and there would be
NO REQUIRED protection for the secondary of the transformer.  Therefore, the Requirements for
TRANSFORMER  protection in T450.3(B) would be met, and assuming the primary and  secondary conductors were already properly protected by the 80A and 200A  OCPDs, reducing the primary OCPD to 70A, the
You are trying to force the
presence of an OCPD on the secondary side of the transformer for the protection of the
secondary conductors as meaning that the Transformer is "Primary and Secondary" protected.  But Table 450.3(B) tells us that the method of protecting the Transformer as "Primary Only" or "Primary and Secondary" is related the Maximum Rating or Setting of the Transformer OCPDs as a Percentage of Transformer Rated current.  In the OP, with a 70A primary OCPD, the "Protection Method" for the transformer would be "
Primary Only," and no Secondary Protection would be required for the
TRANSFORMER.  In this case, the OCPD on the secondary side will only be providing protection to the conductors, not to the transformer.  As such, the rating of the OCPD must be only lower or equal to the ampacity of the secondary conductors.  There is no limit to the OCPD relating to the Percentage of the Transformer secondary current.