If there is low impedance ground fault for that portion of tap which is already intentionally grounded, the increase in current in the primary side of the transformer may actuate the primary protection. But if the impedance of the ground fault is such that the ground fault current exceeds the rating of winding portion of that tap but still not sufficient to operate the primary protection, damage to the transformer may occur. The same logic applies even when any other point in the delta or star is unintentionally grounded when there already exists one 'earth' point in the winding.I am concerned about what happens when there is a fault from the one mentioned phase to the ground that is only going to probably have anywhere between 12 - 72 volts depending on which "H" taps are used.
So additional protection of transformer winding may be needed.