406.12 Tamper-Resistant Receptacles in Dwelling Units.
In all areas specified in 210.52, all nonlocking-type
125-volt, 15- and 20-ampere receptacles shall be listed
tamper-resistant receptacles.
Exception: Receptacles in the following locations shall
not be required to be tamper-resistant:
(1) Receptacles located more than 1.7 m (51⁄2 ft) above the
floor.
(2) Receptacles that are part of a luminaire or appliance.
(3) A single receptacle or a duplex receptacle for two appliances
located within dedicated space for each appliance
that, in normal use, is not easily moved from one
place to another and that is cord-and-plug connected
in accordance with 400.7(A)(6), (A)(7), or (A)(8).
(4) Nongrounding receptacles used for replacements as
permitted in 406.4(D)(2)(a).
Just mount all the receptacles above 5 1/2 feet..:lol:
SABC?
EDIT I guess you could have 5' counter tops!
Was just fixin to fire that one at you!
Just mount all the receptacles above 5 1/2 feet..:lol:
You would still need to install receptacles below 5.5' to satisfy 210.52.
You would still need to install receptacles below 5.5' to satisfy 210.52.
210.52(3) ?
Seems that is all I can find that limits how high I could go as ridiculous as it seems, but we are stuck on the 08 code here in WI.
Other than kitchen counters I could put my general use recepticals at 7' and sill meet code??
Please tell me I am missing something not that I would do this but I bet someone would just to prove a point.
If it's above 5.5' then it doesn't count a receptacle that is required by the 6'/12' wall spacing rule.
If you're under the 2008 then the 5.5' exception does not exist.
Rob
We are debating the 2'/4' wall spacing rule. Counters.
I was commenting on posts #2 and #3 which make no mention of countertops. My comments were directed at the 2011 exception for non-TR receptacles above 5.5". Sorry for the confusion.