kbsparky
Senior Member
- Location
- Delmarva, USA
Here is a real scenario I've encountered:
A new house, with an outside meter combination disconnect box located 25 feet away from the house.
From there, an underground conduit travels to the building, and under the basement slab to a point in the cellar where a transfer switch and load center are located.
On the opposite end of the house, there is a 20 kW standby generator, which has its own 100 Amp breaker/disconnect built-in. It also has an underground conduit that travels under a concrete slab to the same transfer switch in the cellar.
Since both disconnects are located outside, and within sight of the house, is there any requirement for additional disconnecting means at the transfer switch in the cellar?
I have attached a drawing outlining the basic layout.