I had an inpection in nyc last week and the inspector is require me that all the 277/480 conduits need to have bonding locknuts.( the one that have the screw in)
I try to explain him that a bonding bushing is required when you connect your pipe in a concentric or exentric knockout in order to ensure the electrical continuity of the metal raceways.
He agree with it but no matter is you make you own hole a bonding locknut is require!!!
I use only 3/4 size pipe in order to not take any chance with any of my guys for use a 1/2 inch pipe in a 1/2 inch 3/4 knockout.
Also all knockouts for feeders were made by a knockout punch for a proper size.
All my pipes are EMT and if I don't understand wrong 250.97 3 is a clear article in refer to the EMT pipe.
What is your opinion?
I try to explain him that a bonding bushing is required when you connect your pipe in a concentric or exentric knockout in order to ensure the electrical continuity of the metal raceways.
He agree with it but no matter is you make you own hole a bonding locknut is require!!!
I use only 3/4 size pipe in order to not take any chance with any of my guys for use a 1/2 inch pipe in a 1/2 inch 3/4 knockout.
Also all knockouts for feeders were made by a knockout punch for a proper size.
All my pipes are EMT and if I don't understand wrong 250.97 3 is a clear article in refer to the EMT pipe.
What is your opinion?