Hey guys, I recently installed a drive on a 40 hp fan on a large grain dryer. We started testing the dryer a couple days ago and there has been a problem with the ingnition sequence on the burner (the flame sensing probe is not showing a flame). A service tech from the manufacturer came out, replaced the ignition board and the thing worked fine all day yesterday. He did suggest to me that the problem could be VFD noise and reccommended installing a load reactor after the drive. Now, I do have a line reactor in front of the drive, but I thought that load side reactors are specifically for softening the peaks of the voltage to the motor to avoid insulation breakdown? Today i was out there for hours trying different things. First i I tried isolating the ground to the ignition board, isolating the motor ground, isolating the vfd ground (all directly to a ground rod) but had no positive results. Anybody have any thoughts on the situation??? The motor leads were ran by a previous electrician from the dryer controller inside a building about 40 feet away through a pvc conduit with a few other 120 volt control wires. They are routed through a large termination cabinet at the dryer as well (the leads are all at least three inches away from any other data wires and all are shielded cables) . Tomorrow Im thinking about removing the motor feeder from its pvc conduit and totally isolating from the rest of the wires. Any insight would be appreciated!