vfd noise problems???

Status
Not open for further replies.

Rsteenson

Member
Hey guys, I recently installed a drive on a 40 hp fan on a large grain dryer. We started testing the dryer a couple days ago and there has been a problem with the ingnition sequence on the burner (the flame sensing probe is not showing a flame). A service tech from the manufacturer came out, replaced the ignition board and the thing worked fine all day yesterday. He did suggest to me that the problem could be VFD noise and reccommended installing a load reactor after the drive. Now, I do have a line reactor in front of the drive, but I thought that load side reactors are specifically for softening the peaks of the voltage to the motor to avoid insulation breakdown? Today i was out there for hours trying different things. First i I tried isolating the ground to the ignition board, isolating the motor ground, isolating the vfd ground (all directly to a ground rod) but had no positive results. Anybody have any thoughts on the situation??? The motor leads were ran by a previous electrician from the dryer controller inside a building about 40 feet away through a pvc conduit with a few other 120 volt control wires. They are routed through a large termination cabinet at the dryer as well (the leads are all at least three inches away from any other data wires and all are shielded cables) . Tomorrow Im thinking about removing the motor feeder from its pvc conduit and totally isolating from the rest of the wires. Any insight would be appreciated!
 

kwired

Electron manager
Location
NE Nebraska
Hey guys, I recently installed a drive on a 40 hp fan on a large grain dryer. We started testing the dryer a couple days ago and there has been a problem with the ingnition sequence on the burner (the flame sensing probe is not showing a flame). A service tech from the manufacturer came out, replaced the ignition board and the thing worked fine all day yesterday. He did suggest to me that the problem could be VFD noise and reccommended installing a load reactor after the drive. Now, I do have a line reactor in front of the drive, but I thought that load side reactors are specifically for softening the peaks of the voltage to the motor to avoid insulation breakdown? Today i was out there for hours trying different things. First i I tried isolating the ground to the ignition board, isolating the motor ground, isolating the vfd ground (all directly to a ground rod) but had no positive results. Anybody have any thoughts on the situation??? The motor leads were ran by a previous electrician from the dryer controller inside a building about 40 feet away through a pvc conduit with a few other 120 volt control wires. They are routed through a large termination cabinet at the dryer as well (the leads are all at least three inches away from any other data wires and all are shielded cables) . Tomorrow Im thinking about removing the motor feeder from its pvc conduit and totally isolating from the rest of the wires. Any insight would be appreciated!

I don't mean to be a smarty pants, but is the flame sensor rod clean and burner surfaces clean? These flame sensors detect a small voltage that develops between the sensor rod and grounded surfaces of the burner assembly. Corrosion and other build up on these surfaces will effect detection of that voltage. If you suspect the drive is cause of problems can you temporarily run the blower across the line and see if the problems go away? If they don't then you know it is not the drive.
 

Rsteenson

Member
I don't mean to be a smarty pants, but is the flame sensor rod clean and burner surfaces clean? These flame sensors detect a small voltage that develops between the sensor rod and grounded surfaces of the burner assembly. Corrosion and other build up on these surfaces will effect detection of that voltage. If you suspect the drive is cause of problems can you temporarily run the blower across the line and see if the problems go away? If they don't then you know it is not the drive.

I will not take offense to any suggestion at this point haha! I am using the vfd for phase conversion as well as speed control so across the line is not an option unfortunately. I cleaned and drilled out the burner holes and the probe myself....also the dryer tech replaced the probe the other night. I read in the troubleshooting guide for the igition board about grounding the burner directly to the chassis but havent done that just yet.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The motor leads were ran by a previous electrician from the dryer controller inside a building about 40 feet away through a pvc conduit with a few other 120 volt control wires.

Din ding ding... I think we have a winner! :eek:

VFD output conductors are MARVELOUS local radio transmitters, unless their signal is dampened by... grounded metal. You MUST run VFD output cables in metal conduit or use "VFD Cable" that has metallic shields. You will find that information in the installation manuals of all VFDs (from reputable suppliers).

You should also NEVER run other control wires in the output conduits of a VFD, in fact I don't recommend running them in the same conduits as power leads of any sort.
 

mike_kilroy

Senior Member
Location
United States
Rsteenson;1425684The motor leads were ran by a previous electrician from the dryer controller inside a building about 40 feet away through a pvc conduit with a few other 120 volt control wires. .....Tomorrow Im thinking about removing the motor feeder from its pvc conduit and totally isolating from the rest of the wires.[/QUOTE said:
I suspect Jraef's ding ding ding hit the jackpot; your motor leads running 40' with 120v wiring is probably the main culprit. Remove and run separate is likely to fix the issue. Those 600v spikes (1200v if 460v vfd) are guaranteed to get into the 120v wires and be carried to other 120v supplied stuff - like your senstive flame detector that probably is powered off 120v out there..... little hope of this working IMHO.

BTW, the idea to add output reactor is valid, altho it is a bandaid rather than fixing the problem - and prob would not solve YOUR problem with the 40' parallel run wires.... making it 'easier' on the insulation is a SIDE EFFECT of adding the reactor which reduces the voltage spikes from 600/1200v to round 400/900v - so reduces the noise by reducing the voltage (P=V^2/Z you know.....)....
 
Last edited:

Besoeker

Senior Member
Location
UK
I suspect Jraef's ding ding ding hit the jackpot; your motor leads running 40' with 120v wiring is probably the main culprit. Remove and run separate is likely to fix the issue.
Equally importantly or possibly more so is the steel conduit or screened/armoured cable as Jraef has pointed out.
Running the conductors in PVC conduit is like running them in air. I'm a bit surprised that anyone would have done that.
And I don't think an output reactor would do a lot to fix the problem.
 

Rsteenson

Member
Thanks for the input guys. I will pull those wires out first thing this morning and post results tonight. I "ass"umed that only voltage sensitive wires would be affected by the motor leads...hopefully this solves my problem!
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
unless their signal is dampened by... grounded metal.
Jraef, I really get perturbed by smart people confusing damp with dampen ... the latter gets it wet. You meant (I assume) unless their signal is damped by... grounded metal.

I know, sorry to vent ... just so many control theory courses where the instructor threw a glass of water on those of us who forgot ...
 
Hey guys, I recently installed a drive on a 40 hp fan on a large grain dryer. We started testing the dryer a couple days ago and there has been a problem with the ingnition sequence on the burner (the flame sensing probe is not showing a flame). A service tech from the manufacturer came out, replaced the ignition board and the thing worked fine all day yesterday. He did suggest to me that the problem could be VFD noise and reccommended installing a load reactor after the drive. Now, I do have a line reactor in front of the drive, but I thought that load side reactors are specifically for softening the peaks of the voltage to the motor to avoid insulation breakdown? Today i was out there for hours trying different things. First i I tried isolating the ground to the ignition board, isolating the motor ground, isolating the vfd ground (all directly to a ground rod) but had no positive results. Anybody have any thoughts on the situation??? The motor leads were ran by a previous electrician from the dryer controller inside a building about 40 feet away through a pvc conduit with a few other 120 volt control wires. They are routed through a large termination cabinet at the dryer as well (the leads are all at least three inches away from any other data wires and all are shielded cables) . Tomorrow Im thinking about removing the motor feeder from its pvc conduit and totally isolating from the rest of the wires. Any insight would be appreciated!

All the shielding of the motor feeders are valid, but before you do that, you may try to change the carrier frequency to see if it makes any difference. Cheapest and may just be 'good enough', not necessary the right one though and before you run the speed up/down through the range you wouldn't nkow if you 'got it' or not.
 

Besoeker

Senior Member
Location
UK
Jraef, I really get perturbed by smart people confusing damp with dampen ... the latter gets it wet. You meant (I assume) unless their signal is damped by... grounded metal.

I know, sorry to vent ... just so many control theory courses where the instructor threw a glass of water on those of us who forgot ...
I don?t often comment on spelling unless it is funny or alters the meaning in an odd/amusing way. If I did, I'd be fair game for reciprocal posts.
The use and abuse of the English language is prevalent on the internet. Sometimes I see phonetic spelling that takes a little thought to interpret.

Asan example, something I posted in another forum earlier today:

I had a girlfriend who was from Pompey and was teaching in north London.
One child had written the word "betaters" in an essay.
After saying it out loud a few times the meaning dawned on her. What the child meant was "potatoes".
Obvious, init?

You have to hear it with a local accent........

My take is that, as long as the meaning of the post is clear, it conveys the message.
Taking a pop at the poster isn't constructive.
 

Besoeker

Senior Member
Location
UK
All the shielding of the motor feeders are valid, but before you do that, you may try to change the carrier frequency to see if it makes any difference. Cheapest and may just be 'good enough', not necessary the right one though and before you run the speed up/down through the range you wouldn't nkow if you 'got it' or not.
Admittedly quick and cheap. But I wouldn't bet the farm on it.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Jraef, I really get perturbed by smart people confusing damp with dampen ... the latter gets it wet. You meant (I assume) unless their signal is damped by... grounded metal.

I know, sorry to vent ... just so many control theory courses where the instructor threw a glass of water on those of us who forgot ...

I had this argument, in reverse (meaning I took your position), with a prof a long time ago when I was so bold as to have challenged his use as well. I was put in my place by virtue of the fact that Merriam Webster begs to differ;

damp?en verb \ˈdam-pən\
damp?ened damp?en?ing \ˈdamp-niŋ, ˈdam-pə-\
Definition of DAMPEN
transitive verb
1: to check or diminish the activity or vigor of : deaden <the heat dampened our spirits>
2: to make damp <the shower barely dampened the ground>

So as he put it; "You are making a case for the #2 definition to be the first and only. Please take that up with the fine folks at Webster's, not me."
 

pfalcon

Senior Member
Location
Indiana
I had this argument, in reverse (meaning I took your position), with a prof a long time ago when I was so bold as to have challenged his use as well. I was put in my place by virtue of the fact that Merriam Webster begs to differ; So as he put it; "You are making a case for the #2 definition to be the first and only. Please take that up with the fine folks at Webster's, not me."

The dictionary people include words that have been created through usage even when improperly used.

Damp - n. Slightly Wet
Dampen - v. to be made slightly wet
Dampened - past v. - was made slightly wet

Damp - v. to reduce or to deaden
Dampen - ?. to be made to reduce? or to be made to deaden?
Dampened - ?. - was made to reduce? or was made to deaden?
Damped - past v. - was reduced or deadened.

-en adds "to be made" to convert a noun to a verb. Not used to convert a verb to a different verb. But usage trumps proper construction.
 

Besoeker

Senior Member
Location
UK
The dictionary people include words that have been created through usage even when improperly used.

Damp - n. Slightly Wet
Dampen - v. to be made slightly wet
Dampened - past v. - was made slightly wet

Damp - v. to reduce or to deaden
Dampen - ?. to be made to reduce? or to be made to deaden?
Dampened - ?. - was made to reduce? or was made to deaden?
Damped - past v. - was reduced or deadened.

-en adds "to be made" to convert a noun to a verb. Not used to convert a verb to a different verb. But usage trumps proper construction.
Did you have any difficulty in understanding the point Jraef was making?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Agree, but worth a try since it hardly cost a penny....:eek:hmy:

other than your time. but in general, I agree it is probably a good first shot at the problem.

load reactors would be my second shot at it.

redoing the conduit is a pricey thing to do and would take me a while to get to. might be cheaper to just leave the conduit as is and disconnect the VFD wires and run VFD cable seperately.
 

mike_kilroy

Senior Member
Location
United States
pulling the vfd wires and running separate would tell the story though, so worth the effort. but perhaps it would be easier to remove the 120v control wires instead? or just disconnect both ends so vfd cables are alone for the test?

If this solves the issue, perhaps rather than buying shielded vfd cable or metal conduit change, just twisting the 4 motor cables with drill for the whole length and stick in separate pvc might be enough.....

anyway, I do not recall hearing if the vfd motor leads included a 4rth ground wire to motor case or not? If not, it too needs to be added. even shielded vfd wire has 4 wires (if you dont put it in metal conduit, altho here I would run a ground wire too)
 

mike_kilroy

Senior Member
Location
United States
Ha! Actually, this was/is common with some experienced machine tool rebuilders. They just stick the 4 wires into the end of the drill and turn it on while their buddy walks back along the wire and lets it twist itself. They even have standards for how many twists per foot type thing.... makes a really neat looking cable assembly. I've watched in awe while they twist a 50' long set of #6 wires.....
 

Besoeker

Senior Member
Location
UK
Ha! Actually, this was/is common with some experienced machine tool rebuilders. They just stick the 4 wires into the end of the drill and turn it on while their buddy walks back along the wire

Wouldn't you need a fairly large chuck to accommodate four #6 conductors?
 