For a 10kW max system, a 60A disconnect fused at 45A or a 45A MCCB would suffice. Other details would present themselves, such as where and how to tap the service conductors.
If the system is 10kW AC at 240V, it will require a 60A OCPD, due to PV being considered a continuous load.
Unfortuantely AHJ does not permit line side taps for residential.
That is such BS. Do they allow it for the other purposes explicitly permitted by the NEC? AHJs need to get over it. I realize my saying all this doesn't help you.
I thought this would be a very common situation with a common solution? I guess not.
Yeah, the common solution is the line side tap! Or the breaker downsizing.
There are a lot of 200A homes out there. Do most of you PV installers just recommend 7.1KW max systems so you dont' have to mess with this?
I think most installers would try to present two options, the one that requires the upgrade and the one that does not. And do their homework on the supply-side connection option before giving the quote.
I would install a 200 amp fusible disconnect with 175 amp fuses as the service disconnect and connect the load side of the new disconnect to the line side of the 200 amp breaker in the panel. You will also have to relocate the main bonding jumper to the new disconnect and separate the EGCs and neutrals at the existing panel.
This would probably be the cheapest, simplest solution, if the AHJ won't allow a supply side connection.