COMMENT 15-41 517.19(C)(2)
fmtjfw
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 15-41. Thanks, Jim Williams
4 Comment:
red -- delete
517.19 Critical Care Areas.
(C) Operating Room Receptacles
(2) Receptacle Requirements.
The receptacles required in 517.19(C)(1) shall be permitted to be of the single, or duplex or quadruplex types or any combination of both.
5 Statement of Problem and Substantiation.
Hospital grade quad receptacles are available. They are referenced in other receptacle descriptions in 517.
4 Comment:
red -- delete
How about eliminating the simplex, duplex, qud language just in case someone comes up with a 3 plex and just allow them to be of a type listed as hospital grade.
1 of 3 related COMMENT 15-35 517.18(B)
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 15-35. Thanks, Jim Williams
4 Comment:
red is deleted text
517.18 General Care Areas.
(B) Patient Bed Location Receptacles.
Each patient bed location shall be provided with a minimum of eight receptacles. They shall be permitted to be of the single, duplex, or quadruplex type, or any combination of the three. All receptacles shall be listed ?hospital grade? and shall be so identified. The grounding terminal of each receptacle shall be connected to an insulated copper equipment grounding conductor sized in accordance with Table 250.122.
Why chase the additions in receptacle configurations. The important part is ?Hospital Grade?.
2 of 3 COMMENT 0-0 517.19(B)(2)
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 517.19(B)(2). Thanks, Jim Williams
4 Comment:
The receptacles required in 517.19(B)(1) shall be permitted to be single, duplex, or quadruplex type or any combination thereof. All receptacles shall be listed ?hospital grade? and shall be so identified. The grounding terminal of each receptacle shall be connected to the reference grounding point by means of an insulated copper equipment grounding conductor.
3 of 3 COMMENT 15-41 517.19(C)(2)
4 Comment: