gas bonding
JDB3
Working on a remodel. In this particular area they want the gas pipe bonded to the electrical service. When I asked the inspector at what location, he pointed to pipes are on the house side of the meter (the gas meter is not presently installed). Is this the correct point to bond to? Thanks,
Only if there's CSST installed. Then you should be bonding on the house side of the meter. FWIW, politely ask him to cite the code section.
Not meaning to highjack this thread,but would there be an issue with bonding the gas line from a 100 amp sub panel which sits less than 6' from the gas meter?
Perhaps NO.
Bonding of gas piping is contingent upon "likely to become energized".
What if the circuit likely to energize the gas line is the subpanel feeder, or branch circuits originating therein...
250.104(B) said:
The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means.
The NEC does not specify the bonding point. However, with the requirement kicking in for piping installed in or on the building or structure, I assume it best to bond at a point that is in or on the building or structure, rather than some point that is away from the building or structure.
Perhaps NO.
Unfortunately the only thing in this sub panel that would likely energize the gas line would be the 110v for the tankless wh's all other gas related circuits are in the main panel.
Perhaps NO.
If we are talking CSST then it must go to the main panel. I assume he meant CSST using #8
You do realize you can use the EGC's of those circuits??? The NEC does not prohibit multiple circuits EGC's from being bonded to the gas piping.
Perhaps NO.
Both could be correct. 110.3(B)
Any inspectors have a problem with adding some black iron near the main panel like in the pic so he only need 6' to bond?
I would pass it.
I would pass it.
Problem may be the International Gas Code:
7.13.2 CSST. CSST gas piping systems shall be bonded to the electrical service
grounding electrode system at the point where the gas service enters the building.
The bonding jumper shall not be smaller than 6 AWG copper wire or equivalent.
Guess I would NOT pass it! :ashamed1:
Also:
5.There are additional metallic house line requirements when extending house lines through exterior walls. In addition to existing requirements, Columbia Gas of Ohio requires that the piping used on the section of house lines that extends through the exterior walls to connect to the meter setting be a minimum of Schedule 40 steel pipe. This section must be securely anchored inside the structure, which will enhance the stability of the meter setting. It will also simplify the placement of bonding clamps when using CSST products.
http://www.columbiagasohio.com/en/your-business/new-business-service.aspx
For those who would like a copy meter placement go here:
http://www.columbiagasohio.com/Libraries/Info_for_Plumbers/COH-Meter-Placement-Guide.sflb
The problem with this picture is those fittings a generally designed for pipe not multisided fittings. The clamp should be on the pipe not the fitting.
Rick there is no problem with the picture, it is showing an hybrid gas line connection between schedole 40 black pipe and a CSST fitting and a clamp designed specifically for atachment to the nut on the CSST with a UL label and listing of 467.
Hmmm. We have always used 8 AWG, but the gas meter was always on the same wall as the electrical service. I'm gonna have to get with the AHJ on this one.
Hmmm. We have always used 8 AWG, but the gas meter was always on the same wall as the electrical service. I'm gonna have to get with the AHJ on this one.[/QUOTE
Minimum wire size for bonding in residential required by all CSST manufacturers has been set at 6 AWG copper or equivalent.