Thanks for your work out, David. But I want to submit that the question is about the relationship between ampacity and voltage drop and not about a given load current less than the conductor ampacity, in this case 80A, and the resulting voltage drop. If the conductor is loaded to its ampacity at different temperature ratings, the resulting voltage drops will be different, thereby suggesting a close relationship between the two.I'm afraid I don't quite understand his point either. As evidenced by...
But let's try this...
#1 THHN with 60deg terminations has an allowable ampacity of 110, #1 THHN with 75 deg terminations has an allowable ampacity of 130 and, #1 THHN with 90 deg terminations has an allowable ampacity of 150. An 80A load over a distance of 500 feet would have the same voltage drop for all three of these conductors, even though they have different ampacities.