fixture tails
yes i found it some inspector told one of our guys that a fixture tail should be number 12 wire on a 2x4
#18 is the minimum size unless the load is greater than those ampacities listed in Table 402.5. Remember that when the tail conductors are smaller than the branch circuit size there are limits on the tail/conductor length. Are these 6' tails?
yes 6ft tails
same guy want an egc in a piece of greenfield its existing but i would say its longer then 6ft.
he maybe right may have to appeal that one.
yes 6ft tails
If longer than 6' it needs a separate EGC. If it's 3/8" FMC (Greenfield) it cannot be longer than 6'.