infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 26, 2012 #2 Do you have a guess? Fixture wires are covered in Article 402.
G grumpy11 Senior Member Sep 26, 2012 #3 yes i found it some inspector told one of our guys that a fixture tail should be number 12 wire on a 2x4
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 26, 2012 #4 #18 is the minimum size unless the load is greater than those ampacities listed in Table 402.5. Remember that when the tail conductors are smaller than the branch circuit size there are limits on the tail/conductor length. Are these 6' tails?
G grumpy11 Senior Member Sep 26, 2012 #5 yes 6ft tails same guy want an egc in a piece of greenfield its existing but i would say its longer then 6ft. he maybe right may have to appeal that one.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 26, 2012 #6 grumpy11 said: yes 6ft tails same guy want an egc in a piece of greenfield its existing but i would say its longer then 6ft. he maybe right may have to appeal that one. Click to expand... If longer than 6' it needs a separate EGC. If it's 3/8" FMC (Greenfield) it cannot be longer than 6'.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 26, 2012 #7 Is your fixture tail feeding only the one fixture ?
G grumpy11 Senior Member Sep 27, 2012 #9 so the allowable ampacity of a #16 tail to a fixture can only be 8 amps and so on
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 27, 2012 #10 grumpy11 said: so the allowable ampacity of a #16 tail to a fixture can only be 8 amps and so on Click to expand... Yes, you just need to follow the ampacities in the aforementioned table, T402.5.
G grumpy11 Senior Member Sep 28, 2012 #11 that's the way i look at it . just trying to get ready to talk for my ahj . about size wire in fixture tail
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Sep 28, 2012 #12 Also look at 240.5(B)(2).