Sub Panels ?

Status
Not open for further replies.

John120/240

Senior Member
Location
Olathe, Kansas
The other thread got me to wondering. Sub panel with EMT or rigid conduit. I don't think you

can but, Three wires 2 hots, 1 neutral, & use the metallic conduit as the ground ?

Thank You
 
sure you can

sure you can

metallic raceways are listed for grounding, given the proper fittings.

Some jobs spec grounding conductors, then you need wires.

also 517 needs wires.
 
The drawback is that at some point in its lifespan the potential to lose your grounding system on metallic pipeing is has a probability. Back in my construction days ground wires were always in the specs
 