Hi Guys'
I have an installation where i have to supply power to 2 devices which will use 18 amps each continuous i am going to pull 6 #10s (it is 3 phase) and 2 #10 grds in 3/4 emt. The terms are rated 75c can i breaker this at 30 amps ?
Am i right in thinking # 10 rated 40amps ie 90c col x .8 for 4-6 cccs = 32 so can be protected at 30 amp breakers.
And continuous use 18 amps x 1.25 = 22.5 so a 25 amp or 30 amp breaker will work. Thanks for the help
IrelandNewYork